Question
Question: For a certain load true power is 150KW and reactive power is 125KVAr. Find the apparent power. A. ...
For a certain load true power is 150KW and reactive power is 125KVAr. Find the apparent power.
A. 19.5KVA
B. 195.2KVA
C. 275 KVA
D. 25KVA
Solution
Hint:- Apparent power is the total power available to us .
Throughout the question we will denote apparent power by S, true power by P and reactive power by Q.
Therefore, from the power triangle we have relation :
S2=P2+Q2
Using this relation we will find the apparent power.
Complete step-by-step solution :
The above figure is called a power triangle which shows us the relation between true power, apparent power and reactive power.
Apparent power: it is total power available to us for use .
True power: it is the consumed power which is used by the consumer.
Reactive power : it is the unused power available .
As per the relationship between true power, reactive power and apparent power from power triangle we have :
S2=P2+Q2
Let’s do the calculation part now by putting the concerned values in the power equation .
⇒S2=P2+Q2 ⇒S2=(150)2+(125)2 ⇒S2=22500+15625 ⇒S2=38125 ⇒S=38125 ⇒S=195.25KVA (done the square of both P ,Q value, added then and took the square root )
Thus option 2 is correct.
Note:-
True power has units kilowatt(KW) , Apparent power has unit kilo volt ampere and reactive power is calculated in kilo volt ampere reactive . The ratio of true power and apparent power must be kept close to 1 for better power consumption without much losses in the system. If the ratio is not kept close to 1 various other equipment like over excited synchronous motors at no load is added to the system ,to improve the ratio close to 1.