Question
Instrumentation and Process Control Question on Measurement of process variables
Consider the surge drum in the figure. Initially, the system is at steady state with a hold-up V=5 m³, which is 50% of the full tank capacity, Vfull, and volumetric flow rates Fin=Fout=1 m³/h. The high hold-up alarm limit Vhigh=0.8Vfull while the low hold-up alarm limit Vlow=0.2Vfull. A proportional (P-only) controller manipulates the outflow to regulate the hold-up V as Fout=Kc(V−V)+Fout. At t=0, Fin increases as a step from 1 m³/h to 2 m³/h. Assume linear control valves and instantaneous valve dynamics. Let Kcmin be the minimum controller gain that ensures V never exceeds Vhigh. The value of Kcmin, in h−1, rounded off to 2 decimal places, is _____.
Answer
The correct Answers is :0.32 or 0.34 Approx