A 500 watt heating unit is designed to operate from a 115 Volt line. If the line voltage drops to 110 volt, the percentage drop in heat output will be

A

10.20%

B

8.1%

C

8.6%

D

7.6%

Answer

8.6%

Explanation

Solution

By using Pconsumed=(VAVR)2×PRP_{consumed} = \left( \frac{V_{A}}{V_{R}} \right)^{2} \times P_{R}

PConsumed=(110115)2×500=456.6WattP_{Consumed} = \left( \frac{110}{115} \right)^{2} \times 500 = 456.6Watt

So % drop in heat output

=PActualPConsumedPActual×100=(500456.6)500×100=8.6%= \frac{P_{Actual} - P_{Consumed}}{P_{Actual}} \times 100 = \frac{(500 - 456.6)}{500} \times 100 = 8.6\%