Question
Question: \[1{\rm{ MW}}\] power is to be delivered from a power station to a town \[10{\rm{ km}}\] away. One u...
1MW power is to be delivered from a power station to a town 10km away. One uses a pair of Cu wires of radius 0.5cm for this purpose. Calculate the fraction of ohmic losses to power transmitted if a step-up transformer is used to boost the voltage to 11000V, power transmitted, then a step-down transformer is used to bring voltage to 220V. (ρCu=1.7×10−8Ωm).
Solution
Resistance of the copper wire is directly proportional to its length and inversely proportional to the cross-sectional area. We will calculate the resistance so that it can be substituted in the expression for power loss which is the product of resistance and square of the current flowing through the wire. We know that the fraction of power loss is equal to the ratio of power loss to its initial value.
Complete step by step answer:
Given:
The power to be delivered to a town is P=1MW=106W.
The distance of the town from the power station is l=10km=10km×(km1000m)=10000m.
The radius of the copper wire used for power transmission is r=0.5cm×(100cmm)=0.5×10−2m.
The value of voltage achieved using a step-down transformer is V1=220V.
The value of voltage achieved using a step-up transformer is V2=11000V.
The resistivity of copper wire is ρCu=1.7×10−8Ωm.
We are required to find the fraction of losses of power transmitted.
We can easily understand that the length of copper wire to be used will be equal to the distance between town and power station. But it is given that a pair of copper wire is used to transmit power; therefore, we can say that the total length of the wire will be twice of its initial value.
L=2l
On substituting 10000m for l in the above expression, we get:
Let us write the expression for resistance present in copper wire.
R=AρCuL……(1)
Here A is the area of cross-section of copper wire, and it is given as:
A=πr2
On substituting 0.5×10−2m for r in the above expression, we get:
On substituting 1.7×10−8Ωm for ρCu, 20000m for L and 7.85×10−5m2 for A in equation (1), we get:
R=(7.85×10−5m2)(1.7×10−8Ωm)(20000m) ⇒R=4.33ΩLet us write the expression for current when the voltage is stepped down using a step-down transformer.
I1=V1P
Here I1 is the current during the step-down stage.
On substituting 106W for P and 220V for V1 in the above expression, we get:
Let us write the expression for power loss during the step-down stage.
P1=I12R
Here P1 is the power loss during the step-down process.
On substituting 0.45×104A for I1 and 4.33Ω for R in the above expression, we get:
We cannot use this method for the transmission of power.
Let us write the expression for current when the voltage is stepped up using a step-up transformer.
I2=V2P
On substituting 106W for P and 11000V for V2 in the above expression, we get:
We can write the expression for power loss during the step-up stage as below:
P2=I22R
Here P2 is the power loss during the step-up process.
On substituting 90.909A for I2 and 4.33Ω for R in the above expression, we get:
We know that the below relationship gives the fraction of power loss:
F=PP2×100%
On substituting 3.5×104W for P2 and 106W for P in the above expression, we get:
Therefore, the fraction of power loss during transmission is 3.578%.
Note: The value of power loss obtained in the step-down stage is itself more than the power to be transmitted; therefore it is not feasible, and hence we did not consider it while reducing the fraction of power loss.