1MW1{\rm{ MW}} power is to be delivered from a power station to a town 10km10{\rm{ km}} away. One uses a pair of Cu wires of radius 0.5cm0.5{\rm{ cm}} for this purpose. Calculate the fraction of ohmic losses to power transmitted if a step-up transformer is used to boost the voltage to 11000V11000{\rm{ V}}, power transmitted, then a step-down transformer is used to bring voltage to 220V220{\rm{ V}}. (ρCu=1.7×108Ωm{\rho _{Cu}} = 1.7 \times {10^{ - 8}}{\rm{ }}\Omega {\rm{m}}).

Explanation

Solution

Resistance of the copper wire is directly proportional to its length and inversely proportional to the cross-sectional area. We will calculate the resistance so that it can be substituted in the expression for power loss which is the product of resistance and square of the current flowing through the wire. We know that the fraction of power loss is equal to the ratio of power loss to its initial value.

Complete step by step answer:
Given:
The power to be delivered to a town is P=1MW=106WP = 1{\rm{ MW}} = {10^6}{\rm{ W}}.
The distance of the town from the power station is l=10km=10km×(1000mkm)=10000ml = 10{\rm{ km}} = 10{\rm{ km}} \times \left( {\dfrac{{1000{\rm{ m}}}}{{{\rm{km}}}}} \right) = 10000{\rm{ m}}.
The radius of the copper wire used for power transmission is r=0.5cm×(m100cm)=0.5×102mr = 0.5{\rm{ cm}} \times \left( {\dfrac{{\rm{m}}}{{100{\rm{ cm}}}}} \right) = 0.5 \times {10^{ - 2}}{\rm{ m}}.
The value of voltage achieved using a step-down transformer is V1=220V{V_1} = 220{\rm{ V}}.
The value of voltage achieved using a step-up transformer is V2=11000V{V_2} = 11000{\rm{ V}}.
The resistivity of copper wire is ρCu=1.7×108Ωm{\rho _{Cu}} = 1.7 \times {10^{ - 8}}{\rm{ }}\Omega {\rm{m}}.
We are required to find the fraction of losses of power transmitted.
We can easily understand that the length of copper wire to be used will be equal to the distance between town and power station. But it is given that a pair of copper wire is used to transmit power; therefore, we can say that the total length of the wire will be twice of its initial value.
L=2lL = 2l
On substituting 10000m10000{\rm{ m}} for l in the above expression, we get:

L=2(10000m) L=20000mL = 2\left( {10000{\rm{ m}}} \right)\\\ \Rightarrow L = 20000{\rm{ m}}

Let us write the expression for resistance present in copper wire.
R=ρCuLAR = \dfrac{{{\rho _{Cu}}L}}{A}……(1)
Here A is the area of cross-section of copper wire, and it is given as:
A=πr2A = \pi {r^2}
On substituting 0.5×102m0.5 \times {10^{ - 2}}{\rm{ m}} for r in the above expression, we get:

A=π(0.5×102m)2 A=7.85×105m2A = \pi {\left( {0.5 \times {{10}^{ - 2}}{\rm{ m}}} \right)^2}\\\ \Rightarrow A = 7.85 \times {10^{ - 5}}{\rm{ }}{{\rm{m}}^2}

On substituting 1.7×108Ωm1.7 \times {10^{ - 8}}{\rm{ }}\Omega {\rm{m}} for ρCu{\rho _{Cu}}, 20000m20000{\rm{ m}} for L and 7.85×105m27.85 \times {10^{ - 5}}{\rm{ }}{{\rm{m}}^2} for A in equation (1), we get:

R=(1.7×108Ωm)(20000m)(7.85×105m2) R=4.33ΩR = \dfrac{{\left( {1.7 \times {{10}^{ - 8}}{\rm{ }}\Omega {\rm{m}}} \right)\left( {20000{\rm{ m}}} \right)}}{{\left( {7.85 \times {{10}^{ - 5}}{\rm{ }}{{\rm{m}}^2}} \right)}}\\\ \Rightarrow R = 4.33{\rm{ }}\Omega

Let us write the expression for current when the voltage is stepped down using a step-down transformer.
I1=PV1{I_1} = \dfrac{P}{{{V_1}}}
Here I1{I_1} is the current during the step-down stage.
On substituting 106W{10^6}{\rm{ W}} for P and 220V220{\rm{ V}} for V1{V_1} in the above expression, we get:

I1=106W220V I1=0.45×104A{I_1} = \dfrac{{{{10}^6}{\rm{ W}}}}{{220{\rm{ V}}}}\\\ \Rightarrow{I_1} = 0.45 \times {10^4}{\rm{ A}}

Let us write the expression for power loss during the step-down stage.
P1=I12R{P_1} = I_1^2R
Here P1{P_1} is the power loss during the step-down process.
On substituting 0.45×104A0.45 \times {10^4}{\rm{ A}} for I1{I_1} and 4.33Ω4.33{\rm{ }}\Omega for R in the above expression, we get:

P1=(0.45×104A)2(4.33Ω) P1=0.81×106W{P_1} = {\left( {0.45 \times {{10}^4}{\rm{ A}}} \right)^2}\left( {4.33{\rm{ }}\Omega } \right)\\\ \Rightarrow{P_1} = 0.81 \times {10^6}{\rm{ W}}

We cannot use this method for the transmission of power.
Let us write the expression for current when the voltage is stepped up using a step-up transformer.
I2=PV2{I_2} = \dfrac{P}{{{V_2}}}
On substituting 106W{10^6}{\rm{ W}} for P and 11000V11000{\rm{ V}} for V2{V_2} in the above expression, we get:

I1=106W11000V I1=90.909A{I_1} = \dfrac{{{{10}^6}{\rm{ W}}}}{{11000{\rm{ V}}}}\\\ \Rightarrow{I_1} = 90.909{\rm{ A}}

We can write the expression for power loss during the step-up stage as below:
P2=I22R{P_2} = I_2^2R
Here P2{P_2} is the power loss during the step-up process.
On substituting 90.909A90.909{\rm{ A}} for I2{I_2} and 4.33Ω4.33{\rm{ }}\Omega for R in the above expression, we get:

P2=(90.909A)2(4.33Ω) P2=3.5×104W{P_2} = {\left( {90.909{\rm{ A}}} \right)^2}\left( {4.33{\rm{ }}\Omega } \right)\\\ \Rightarrow{P_2} = 3.5 \times {10^4}{\rm{ W}}

We know that the below relationship gives the fraction of power loss:
F=P2P×100%F = \dfrac{{{P_2}}}{P} \times 100\%
On substituting 3.5×104W3.5 \times {10^4}{\rm{ W}} for P2{P_2} and 106W{10^6}{\rm{ W}} for P in the above expression, we get:

F=3.5×104W106W×100% F=3.578%F = \dfrac{{3.5 \times {{10}^4}{\rm{ W}}}}{{{{10}^6}{\rm{ W}}}} \times 100{\rm{ }}\% \\\ \therefore F = 3.578{\rm{ }}\%

Therefore, the fraction of power loss during transmission is 3.578%3.578{\rm{ }}\% .

Note: The value of power loss obtained in the step-down stage is itself more than the power to be transmitted; therefore it is not feasible, and hence we did not consider it while reducing the fraction of power loss.